    HI GUYs

     

    I would like to set up scenario: when i switch on the light in bathroom the ventilation should be delayed 5 minutes from that moment than it should start working

    now 1. If i switch off the light within the first 5 min  I dont want to switch on the ventilation at all.

    2. if the light is switched on for  5 minutes the ventilation should start working.

    3. If the lights is switched off anytime after the 5 minutes I want to vents to continue for next 10 minutes then switch off

     

    Shall I use variables ?




    User
    milosek
    Role
    End User
    12 posts
    Verified

    Hi Milosek,

    You will need 2 scenarios.

    Scenario 1 – Start=Light ON   Only If=Empty   Action=Delay 5min – Fan ON  Stop=Light OFF

    Scenario 2 – Start=Light OFF   Only If=Fan is ON    Action=Delay 10min – Fan OFF   Stop=Light ON




    User
    eugeneduffy
    Role
    Wholesaler
    74 posts